hadi Oluşturuldu: 27 Nisan, 2022 Share Oluşturuldu: 27 Nisan, 2022 Hello I download my program on TSG 070E But macro files don't execute on trigger times (timer with 500ms execution cycle) ? it seems macros didn't download to HMI. Offline simulation works correctly with these macro. thanks for your help Alıntı Yorum bağlantısı Sitelerde Paylaş More sharing options...
Hanifi 28 Nisan, 2022 gönderildi Share 28 Nisan, 2022 gönderildi Hi, please add your project in here to analysis what the the real problem is. Alıntı Yorum bağlantısı Sitelerde Paylaş More sharing options...
hadi 28 Nisan, 2022 gönderildi Yazar Share 28 Nisan, 2022 gönderildi 3 hours ago, Hanifi said: Hi, please add your project in here to analysis what the the real problem is. thanks I create this test file that uploaded here, macro works fine in simulation but not in HMI ! https://www.mediafire.com/file/iauwwiwy5g6y9md/Test.rar/file Alıntı Yorum bağlantısı Sitelerde Paylaş More sharing options...
Hanifi 28 Nisan, 2022 gönderildi Share 28 Nisan, 2022 gönderildi 4x2019 is double word register but in macro code it is selected as word format. Please change it in macro varible section as signed int or insigned int. Btw, The macro code will not execute if the communication is not existing or well between HMI and PLC. Because Macro has PLC register. Alıntı Yorum bağlantısı Sitelerde Paylaş More sharing options...
hadi 28 Nisan, 2022 gönderildi Yazar Share 28 Nisan, 2022 gönderildi 43 minutes ago, Hanifi said: 4x2019 is double word register but in macro code it is selected as word format. Please change it in macro varible section as signed int or insigned int. Btw, The macro code will not execute if the communication is not existing or well between HMI and PLC. Because Macro has PLC register. thanks it works Alıntı Yorum bağlantısı Sitelerde Paylaş More sharing options...